Storage: Power shifting
This strategy consists in storing part of the available PV energy during the day and discharging it later during periods of higher electricity tariffs.
Principle
The user can specify charging conditions (charging hours, charging power or charging fraction of PV production) and discharging conditions (hours and discharging power). Discharging is typically scheduled during periods with higher tariffs, or when required by the grid operator. In this mode, no local (on-site) consumption is considered: the energy flows are comparable to those in the peak shaving strategy.
In systems subject to grid export limitations, power shifting can also act partially as a peak-shaving strategy: when PV generation exceeds the permitted injection, the surplus can be diverted to the battery. This approach is designed for large-scale, utility-connected projects to optimize revenues. It does not currently support self-consumption in PVsyst, though this may be added in future versions if needed. For the strategy to be economically viable, the cost of stored energy must be lower than the tariff difference between peak and off-peak hours.
Storage_Powershift
Charging Strategies
Three charging strategies are available and can be defined either on a daily or hourly basis:
  • Fraction of the PV production: a fixed fraction of the available PV power is directed to the battery. Note that the fraction is applied to the expected nominal EArray, not to EoutInv.
  • Fixed charging power: the battery is charged at a constant power setpoint. Any remaining available PV power is injected into the grid. If PV production is lower than the setpoint, all generated energy is sent to the battery, but the target charging power will not be reached. Note that losses apply: when sending 50 kW to the battery, charging losses occur, and the energy actually stored is slightly less.
  • Fixed grid export: a fixed power is injected into the grid, and any surplus PV energy is used to charge the battery. If PV production is lower than the fixed export setpoint, all energy is sent to the grid, but the target injection will not be reached.
The table below illustrates (no losses shown) how PV power is split between the battery and the grid for each strategy. This split assumes the battery can accept charge; when the battery is full, all surplus energy is sent to the grid. Note that the charge is also limited by the charger maximum charging power.
PV Production [kW] Fixed grid export: 100 kW Fixed charging: 100 kW Fraction: 40%
Grid [kW] Battery [kW] Grid [kW] Battery [kW] Grid [kW] Battery [kW]
50 50 0 0 50 30 20
100 100 0 0 100 60 40
150 100 50 50 100 90 60
300 100 200 200 100 180 120
Note: The power shifting mode is compatible with grid limitations. The Fixed grid export strategy can be used as a peak shaving mechanism.
Discharging Strategies
Two discharging strategies are defined to control when and how the battery releases stored energy.
  • Specified hours: the battery discharges at a fixed power during the selected time slots. Different discharging powers can be assigned to different periods.
  • During the night: the battery discharges overnight, with night hours determined from the weather data (.MET file) used in the simulation. During dusk/dawn hours, the battery will discharge during the corresponding fraction of hour after sunset.
Procedure and Sizing
  • Define the charging and discharging conditions: Once the strategy is selected, you have two main options: Daily profile or CSV import.
    • Daily profile
      • If power per hour is not checked, you can specify one unique value and the half-hours to which the value applies using the dial. For simulations using an hourly time step, any half-hour selected will be interpreted as half the fixed value over the entire hour.
      • When checked, you can specify a different value for each hour.
    • Defined from file
You can load a file containing variable values for any of these strategies by selecting "Defined from file" and clicking on Choose CSV file. This opens the standard parameter import window.
Charging Sizing: PVsyst displays the expected charging energy on a clear summer or winter day, which provides a reference for sizing the battery pack.
Discharging Sizing: The possible discharging energy per day should be close to or greater than the charging energy to ensure full daily cycling.
charging_hours
  • Battery pack definition: In the storage pack tab, select a battery model and define the number of cells/modules in series (operating voltage to match charger/inverter requirements) and in parallel (storage capacity). Sizing: Battery size is determined by the desired daily energy shift, which is an economic choice. Optimization typically involves running multiple simulations to compare tariff differences (direct vs. stored kWh over the battery lifetime) with the battery system cost. Because shifting is limited to daily cycles, battery capacity should not exceed the maximum daily charging energy.
  • Define the maximum charging power Once the storage pack is defined, specify the charger nominal power in the power shifting tab. The default is derived from the charging strategy for a clear day and is limited by the battery’s maximum charging power. Oversizing should be avoided, as efficiency depends on the operating point relative to the efficiency curve. The maximum charging power should be higher than the power to be charged, as losses occur during charging.
  • Define the maximum discharging power Finally, specify the nominal output power of the battery inverter. The default value is based on the maximum discharging power from the strategy and is limited by the battery’s maximum rating. The maximum discharging power should be higher than the power to be discharged to the grid, as losses occur during discharge.
Grid limitation
Grid limitations (if any) should be applied at the injection point and not at the inverter level. If the battery is full and the grid limitation is reached, the lost energy will be accounted as EGridLim. Note that in the peak shaving strategy, this quantity is accounted as EUnused.
Simulation
The battery operates in daily cycles: it is discharged overnight and recharged during the day according to the chosen strategy.
After the simulation, the energy fluxes will be displayed in the loss diagram:
Storage_Results_PowerShifting
The diagram shows:
  • Stored and direct use: fraction of available energy stored in the battery.
  • Battery global loss: difference between charging and discharging energies (due to Faradaic efficiency, internal resistance, self-discharge, or gassing in lead-acid batteries). This indicates the round-trip efficiency.
  • CL_Chrg, CL_InvB: charger and battery inverter efficiency losses.
  • Stored and direct energies: energies at the grid injection point. This is the main result for tariff-based financial evaluation.
  • E_Grid: total energy delivered to the grid.
Updates
  • Added to PVsyst 8.0.17. Not compatible with self-consumption.